So I've made a bit of a discovery. I've said before that the Philips CPO-TW lamps for 45 and 60W look identical, same size arc tube. Well I've gotten hold of an energy monitor and these are the results for the identical looking 45 and 60W lamps:

CPO 60W on 60W ballast = 66W (60W + 6 ballast loss)
CPO 45W on 45W ballast = 66W (60W + 6 ballast loss) Exactly the same!
CPO 45W on 45W ballast with permanent dim to 55% = 51W (45W + 6 ballast loss)

I used three of each ballast and took an average but they were all within 1 or 2 watts anyway. Two of the three runs had a brand new lamp, the third had a used lamp (~3 years nightly service), the used lamp didn't affect the power.

Also visually, the 60 and 45 at full power seemed to be pretty much identical in terms of brightness. The 45W on the permanent dim ballast was noticeably dimmer.

So it seems like the 45 and 60W CPO lamps are literally identical, and the 45 is just a 60 with a different etch. To get 45W out of a 45 you need to run it with a permanent dim ballast.